Devicenet Beckhoff BK5220

Adept SmartController CX, assistance, configuration, etc

Devicenet Beckhoff BK5220

Postby WallE » Fri Nov 06, 2015 6:34 am

Hello we are using a Beckhoff BK5220 Devicenet module with the Smartcontrolelr. If we use Adept ACE (current version) the output signals toggle randomly. If I use Adept Desktop or disconnect ACE this behaviour does not occur. What is the Problem?
WallE
 
Posts: 5
Joined: Thu Apr 02, 2015 5:52 am

Re: Devicenet Beckhoff BK5220

Postby Guenter Grass » Tue Nov 10, 2015 1:36 am

Hi WallE,

are the outputs toggled if no tasks are running?

Please stop all tasks that your application is using and have a look at the outputs.


Regards
Günter
Guenter Grass
 
Posts: 189
Joined: Thu Oct 16, 2008 4:34 am

Re: Devicenet Beckhoff BK5220

Postby WallE » Mon Nov 16, 2015 1:38 am

No it stops. Does it mean I got a Software bug. The strange thing is that it does not occur if i use Adept Desktop
WallE
 
Posts: 5
Joined: Thu Apr 02, 2015 5:52 am

Re: Devicenet Beckhoff BK5220

Postby WallE » Mon Nov 16, 2015 1:54 am

oh and it is not shown in the Digital IO Window
WallE
 
Posts: 5
Joined: Thu Apr 02, 2015 5:52 am

Re: Devicenet Beckhoff BK5220

Postby Guenter Grass » Mon Nov 16, 2015 2:11 am

Hi WallE,

I can't say for sure but I assume that the global ACE variables "interact" with your software. Meaning ACE uses global variables with the same name as you do.

Please make sure to avoit REAL(DOUBLE) and STRING variables that start with
"ca."
"fw."
"rm."
"sp."
"sv."

To check reboot the controller and connect with Adept Desktop. Then load you application and look at the global variables either in the Variable Manager or from the Monitor Terminal with
LISTR
LISTS


Regards
Günter
Guenter Grass
 
Posts: 189
Joined: Thu Oct 16, 2008 4:34 am


Return to SmartController CX Robot Control